Socket switch stopped working

I have a socket switch that powers my electric shower. It started smelling “fishy” and the socket/switch was very warm/hot. Now it has stopped working. The switch turns to ‘on’ position but there is no power. How can this be repaired cost effectively?

Asked by Wayne on 19th Apr 2020
Expert Trade Answers
"What you have or should have is an Isolator that makes and brakes the power to the shower. This can either be via a 45 amp double pole pull switch or wall mounted like a cooker switch.
This is a classic example of arcing, where the terminals in the switch are not tight and when drawing 40 to 50 amps of power arcing occurs which causes heat and heat causes fire. I'd bet the internal moulding and terminals in the switch are also burnt out as I've seen this many times. I have pictures of this also, so the way forward is a new Isolator and possibly some of the cable may need replacing as the heat causes the cable to go brittle."
Answered on 19th Apr 2020 - Member since Jan 2020 - report
"The fishy smell is in indication there is a heating of cable either by arcing due to a loose connection or overloading from shower due to under sized cable, this would need to be investigated to ensure the electrical safe guards are in place so that it doesn't reoccurre. It would be prudent to call an Electrician to investigate."
Answered on 19th Apr 2020 - Member since Oct 2018 - report
"Hi Wayne
There is a problem with the switch and it requires a replacement switch as it can cause a short circuit if stuck on the middle position. A replacement switch can be installed for under £100 including labour and materials."
Answered on 19th Apr 2020 - Member since Nov 2019 - report
"You will need to have a insulation test done on the cable, the appliance tested and also have the socket looked at.
From what your saying:
1: I hope it’s a pull cord switch.
2: if you ISOLATE THE POWER. Take off the switch plate and see if it’s fried,
The hot sensation means the cable is more than likely not adequate for the shower unit but without looking at it it’s hard to diagnose as there could several issues, even down to a faulty unit.

Did your board trip?"
Answered on 19th Apr 2020 - Member since Jan 2018 - report
"Replace the switch/pullcord unit. Make sure all contacts are tight."
Answered on 19th Apr 2020 - Member since Sep 2019 - report
"Get an electrician to remove & replace the socket. They'll check the cable for damage, and test the circuit.
All being well, looking at around £75 including minor works cert."
Answered on 19th Apr 2020 - Member since Mar 2018 - report
"Change the switch , burnt out , regards bs electrical"
Answered on 19th Apr 2020 - Member since Oct 2019 - report
"yes most likely switch has burnt out cost new 1 under20 cost to replace 40 total 50 to 60"
Answered on 19th Apr 2020 - Member since Mar 2020 - report
"Commonly with shower switches, terminations where cables are connected may be loose which causes the conductor to burn which may be the reason for the smell. In a good case there may be enough slack on the cable to salvage it. Otherwise your looking at a rewire."
Answered on 20th Apr 2020 - Member since Feb 2020 - report
"Have you had a new shower fitted?
If so it maybe to hi wattage!
Or it has simply just old and warn out and will just need replacing( most common)"
Answered on 19th Apr 2020 - Member since Jan 2018 - report
"Sounds like you need new switch due to loose connection within switch would need to view depends how badly burnt/damaged cable is"
Answered on 19th Apr 2020 - Member since Apr 2019 - report
"Hi there,

It sounds as if the main fuse breakers blown. Its blown for safety reasons, you will need to call out a qualified electrician."
Answered on 19th Apr 2020 - Member since Feb 2018 - report
"A loose connection inside the switch, causing it to heat up and ultimately fail.
A new switch is required and possibly new cable if it shows signs of melting."
Answered on 19th Apr 2020 - Member since Jun 2016 - report
"You need a qualified electrician immediately!
can turn it off at the circuit breaker?
The fishy smell is normally the cable over heating and this is serious as It will eventually result in an electrical fire!!!
From The description you give is quite hard to advise without investing, you need an electrician to investigate, I can only speculate.
I assume when you say socket/switch you are talking about a pull cord switch.
This Fishy smell can be caused by a few different things.
A lose connection in the switch could be the issue causing the switch to seize and this could also give the fishy smell although it is quite common on shower circuits that a plumber or handy man has upgraded the shower to a larger KW shower to the one the cable was originally designed for without carrying out the required electrical calculations and design, This could also cause the fishy smell as the cable is too small for the power required for the new shower.
Please consult a qualified electrician, electricity is deadly in untrained hands!!!"
Answered on 19th Apr 2020 - Member since Jun 2019 - report
"There must me loose connection . You should’ve use shower till is replaced. The switch needs replacing ASAP"
Answered on 19th Apr 2020 - Member since Jan 2020 - report
"Hi Wayne,

Usually the fishy smell is a symptom of the plastic sheathing around the cables breaking down... usually as a result of poor electrical connections; due to the increased resistance it can cause extra heat which makes the cables / switch break down faster until one day it shorts out and won't work anymore!

Depending on the extent of the damage you might be lucky and it could be the isolating switch that has gone faulty and you can just replace that. Otherwise it could be extensive cable damage and would require a more in-depth assessment.

If you're competent and up for the job you could isolate the circuit at the fuse board (distribution board) unscrew the switch and take a look at the connections to see if its the switch that failed or if you can see any cracked cables... If unsure, take a photo and re-post and I'm sure you'll get some more advice!"
Answered on 19th Apr 2020 - Member since Jan 2020 - report
"isolated at consumer unit and get a electrican to repar
the fish smell is the cable burning in the switch"
Answered on 19th Apr 2020 - Member since Mar 2020 - report
"The cause is heat and happens as a result of a loose connector, frequently the neutral (blue) as this vibrates under load. Sometimes it is the silica (mica) insulation that when it gets hot gives off a 'fishy' smell. Look for signs of burning around the connection block. Get an electrician in now to repair will save a higher cost later."
Answered on 20th Apr 2020 - Member since Apr 2020 - report
"Need new Shower unit looks like that one is burnt out"
Answered on 19th Apr 2020 - Member since Mar 2017 - report
"there is a short circuit where it hid, so it is necessary to check a circuit evaluation of this work can be around £ 100-120"
Answered on 19th Apr 2020 - Member since Dec 2019 - report
"You need to replace it after inspection , maybe yougotta water leak ? Get an electrician to do an inspection!"
Answered on 20th Apr 2020 - Member since Feb 2020 - report
Find Tradespeople, compare up to 3 quotes!
It's FREE and there are no obligations
Ask a Trade
Got a question that only a tradesperson can answer? We have thousands of trades ready to answer any question you may have.
Ask your question
Ask a Trade

Are you looking for advice on a DIY project or have a question for our tradespeople?

We'll email your question to tradespeople who are skilled in your chosen category.

Your question will be made public - please do not include any personal details.

{{ first(ask.errors)[0] }}

By continuing you agree to the Community Guidelines.

Report Content

{{ first(reportForm.errors) }}

Thank you

Your report has been created and will be investigated shortly.

Ready to get a price for your home improvement project?
Get started

Over 1 million homeowners and over 50,000 tradespeople
use MyJobQuote nationwide each year