New 16amp 3.6kW oven install

Want a new oven installed. Old one was 13amp connected via plug. Have 6mm cable attached to 40amp on circuit breaker already supplying induction hob. New oven is 3.6kW 16amp.

From what I've looked at i think I do not need new wire from circuit board. Is this correct?

Asked by Vicky on 25th Jun 2025
Expert Trade Answers
"Is the oven going on the same circuit as the hob? The 40 amp fed from the 6mm cable? Technically, depending on how the cable is run, the 6mm may not be sufficient enough to carry 40 amps and should be on a 32 amp, connecting a 16 amp 3.6 kw to this would likely blow the breaker, seeing as the induction hob is potentially 6kw meaning your total power is 9.6kw, personally I would give them separate circuits"
Answered on 25th Jun 2025 - Member since Apr 2023 - report
"Afternoon ,yes you are correct you will required a new 20amp designated circuit fro.m your consumer unit to the kitchen with a 20amp isolation switch ."
Answered on 25th Jun 2025 - Member since Feb 2017 - report
Find Tradespeople, compare up to 3 quotes!
It's FREE and there are no obligations
Ask a Trade
Got a question that only a tradesperson can answer? We have thousands of trades ready to answer any question you may have.
Ask your question
Ask a Trade

Are you looking for advice on a DIY project or have a question for our tradespeople?

We'll email your question to tradespeople who are skilled in your chosen category.

Your question will be made public - please do not include any personal details.

{{ first(ask.errors)[0] }}

By continuing you agree to the Community Guidelines.

Report Content

{{ first(reportForm.errors) }}

Thank you

Your report has been created and will be investigated shortly.

Ready to get a price for your home improvement project?
Get started

Over 1 million homeowners and over 50,000 tradespeople
use MyJobQuote nationwide each year