Difference between an RCD and circuit breaker

What's the difference between an RCD and a circuit breaker? Or are they the same thing?

Asked by Michael on 23rd Jan 2023
Expert Trade Answers
"An MCB is an overload device, designed to operate if there is a short circuit fault or if the current being used on the circuit exceeds the rated current of the device. For instance, you have too many appliances being used at the same time, or if a cable is damaged causing a direct short between live and earth, or live and neutral.
An RCD on the other hand is not an overload device, it is designed operate under current leakage faults, it limits the amount of current that can flow in the event of an electric shock. If electricity if flowing down an unintended path, like yourself, the RCD will detect this and trip out. In households the RCD is limited to 30mA, as it only takes 50mA to stop your heart."
Answered on 23rd Jan 2023 - Member since Jan 2023 - report
"The circuit breaker protect the electrical wiring and system in the property,
the RCD or RCBO protects people from getting an electric shock or electrocution"
Answered on 24th Jan 2023 - Member since Dec 2022 - report
"A circuit breaker trips out when there's a live to earth/ live to neutral fault or on overload

An RCD trips out when there is an earth to neutral fault"
Answered on 5th Feb 2023 - Member since Feb 2023 - report
"An RCD is short for residual current device and protects against electric shock in the event if a fault on either the circuit or applicance. A circuit breaker protects the circuit from current overload and will trip if it's maximum stated current (e.g. 32 amp) is exceeded."
Answered on 2nd Feb 2023 - Member since Jan 2023 - report
"They are both generic terms, and each one can mean more than one thing, however generally in a domestic setting, an RCD is a device which disconnects the supply when a residual current is detected (hence R C D) but a circuit breaker (for example an MCB) is a device which disconnects the supply when an overcurrent is detected. Usually RCDs don't protect from overcurrent and need to be used in conjunction with an MCB.

However nowadays, most electricians tend to fit RCBOs instead, which are a combination of an RCD and an MCB. These protect you from earth leakage as well as overcurrent. This avoids having an RCD protecting several different circuits which isn't ideal as accumulative minor faults can cause nuisance tripping."
Answered on 23rd Jan 2023 - Member since Oct 2022 - report
"Both forms of protection however a breaker will only trip out on overload or short circuit

And a rcd will only trip out on earth leakage or earth related faults

To get the best of both worlds use either rcbo's or mcbs which are protected by rcds"
Answered on 23rd Jan 2023 - Member since Jan 2023 - report
"Hi
A rcd protect a person from accidents a circuit breaker protect the wiring"
Answered on 23rd Jan 2023 - Member since Aug 2018 - report
"rcbos are a circuit breaker version of a rcd.... They are not the same thing.... Rcbos and rcds are very similar if not almost the same in practical terms."
Answered on 6th Feb 2023 - Member since Feb 2022 - report
"Rcd is fault protection.

Basic protection is mcbs"
Answered on 28th Jan 2023 - Member since Jan 2023 - report
"A residual current device is a safety device that must be in place in order to work on any circuit be it an RCD additional to a MCB or RCBO."
Answered on 24th Jan 2023 - Member since Jan 2023 - report
"An RCD will activate on fault current therefore protecting the user from a potential fatal shock, and MCB will work on overload protecting the installation. There's a device called an RCBO which combines the duty of both the MCB and RCD.

hope you find this information useful."
Answered on 23rd Jan 2023 - Member since Dec 2022 - report
Find Tradespeople, compare up to 3 quotes!
It's FREE and there are no obligations
Ask a Trade
Got a question that only a tradesperson can answer? We have thousands of trades ready to answer any question you may have.
Ask your question
Ask a Trade

Are you looking for advice on a DIY project or have a question for our tradespeople?

We'll email your question to tradespeople who are skilled in your chosen category.

Your question will be made public - please do not include any personal details.

{{ first(ask.errors)[0] }}

By continuing you agree to the Community Guidelines.